Thermostat question

Good morning, I hope someone can help. I have an old CD6 Satellite can drink machine (model 3038-51) I recently had the compressor replaced. The compressor came off of another vending machine that was being used for parts. Both compressors are the same 1/4 HP. It runs and cools great. The problem is, it doesn't cut-off. it keeps on running. I have turned the thermostat all the wy off and the compressor will shut off. Would it help if I install the thermostat that was with the machine that I took the compressor off of ? The tech that did the work is not willing to come back. Thanks in advance for your help.

VendingMix
Offline
Last seen: 4 years 2 weeks ago
Joined: 12/07/2012 - 20:01
Thermostat bad?

westvend2002,
Swapping in the other thermostat is the first thing I would try.